Hi Team,
We have an PA-5260 deployed in our environment.
Need to monitor the firewall using SNMP manager for power failure or when the power supply removed.
Firewall is running on PAN-OS 10.0 and we had downloaded the MIB file from the below link and loaded the MIB file for PANTraps
https://docs.paloaltonetworks.com/resources/snmp-mib-files
But we are unable to find the power related OID on the PAN-TRAPS MIB file as given below:
https://knowledgebase.paloaltonetworks.com/KCSArticleDetail?id=kA10g000000ClbfCAC
Will we be able to monitor the Power supply status of the firewall using SNMP or this feature is not available yet .
Thanks in advance
06-15-2022 07:46 PM
Hi @tamilvanan , the ENTITY-STATE-MIB provides data for line cards, fan trays, and power supplies. However, it is currently only used for the PA-7000 and PA-5450 firewalls.
Please reach out to your local SE for assistance in submitting a feature request if this is something you require. There may be more people requiring the same thing.
Thanks.
06-15-2022 09:50 PM
Hi @JayGolf . Thanks for the response.
Is the below provided MIB in PANTRAPS as per documentation only applicable to PA 7000 and PA-5450
https://knowledgebase.paloaltonetworks.com/KCSArticleDetail?id=kA10g000000ClbfCAC
Example OID's | attribute |
.1.3.6.1.4.1.25461.2.1.3.2.0.911 | Power Supply inserted |
.1.3.6.1.4.1.25461.2.1.3.2.0.912 | Power Supply removed |
.1.3.6.1.4.1.25461.2.1.3.2.0.913 | Power Supply failure |
Also the ENTITY-STATE-MIB is used for monitoring the power supply status.
Thanks in advance
10-14-2022 08:27 AM
Hello,
For state of power source, ENTITY-STATE-MIB can be used.
ex. “snmpwalk -On -v2c -c public <ip> .1.3.6.1.2.1.131.1.1.1.ID*”
This oid shows state of power supply module and its alarm state
“.1.3.6.1.2.1.131.1.1.1.3(EntityOperState).ID*” shows power state. 3(Active) is ,2(Idle = power is not coming)
“.1.3.6.1.2.1.131.1.1.1.4.ID*” shows alarm state as “major” when one of power supply does not get power.
Be mindful that PS Object ID(=ID* above) are different in models PA3260 uses 4 and 5 , PA5220 have 9 and 10 for PS1 and PS2 /PA7050 uses 39-42/PA7080 uses 34-41 , etc..
Best Regards,
Romain