PA-3220 Power Supply Air Flow Direction Optional?

cancel
Showing results for 
Show  only  | Search instead for 
Did you mean: 

PA-3220 Power Supply Air Flow Direction Optional?

L0 Member

As I have encountered and many others may also, when this unit was installed in a data center, the person did not follow hot and cold isle standards. Is there an option to replace only the power supply or type of fans to reverse the air flow? This would be much easier than unracking and recabling everything.

1 REPLY 1

Cyber Elite
Cyber Elite

Hello,

I would first check the temps of the device. Typical data centers still have a pretty cool hot aisle.

 

https://knowledgebase.paloaltonetworks.com/KCSArticleDetail?id=kA10g000000ClxkCAC

 

Might save some work.

 

Regards,

  • 2466 Views
  • 1 replies
  • 0 Likes
Like what you see?

Show your appreciation!

Click Like if a post is helpful to you or if you just want to show your support.

Click Accept as Solution to acknowledge that the answer to your question has been provided.

The button appears next to the replies on topics you’ve started. The member who gave the solution and all future visitors to this topic will appreciate it!

These simple actions take just seconds of your time, but go a long way in showing appreciation for community members and the LIVEcommunity as a whole!

The LIVEcommunity thanks you for your participation!